    Anonym
    Inactive

    Hi, I got these Opensprinkler Bought AC version (power connector in orange) and Hunter VAC valves.

    Unfortunately I can't get the valves to work.

    I have connected one wire of the valve to Zone 1 and the other to COM.
    As soon as I Opensprinkler the valve “clicks” at the power connection. So opens? And it gets very warm/hot after 2-3 minutes.
    If I now want to open zone 1 via app, nothing happens...

    The version (AC) should be correct right?

    Am I doing something wrong?

    Thank you

     

    #24082
    adminadmin
    Administrator

    What power supply are you using? It must be a 24VAC - NO 24VDC !!

    Whenever all valves open immediately after switching on, then it seems to be the wrong power supply unit, because the triacs used need a zero crossing to switch, which only works with AC voltage.

    Disconnect immediately OpenSprinkler from the (wrong) power pack because of the high current flow OpenSprinkler and solenoid valves dangerously overloaded.

     

    #24084
    Anonym
    Inactive

    Thanks, stupidly I actually connected an AC/DC power supply :-/
    I didn't see that until I read the "fine print".

    Thanks for the tip.